I'm upgrading a split service (100 amps each) into 1 service, that is, one meter and one new 200 amp panel. The only way to accommodate the new panel is to move it 2 feet to the right (because of a new washer/dryer install). Therefore, I have to extend all the branch circuits to the new panel, as they will not reach as they are. I'm using a 2 foot wire trough with knockouts to gather all the existing wires, and splicing them inside the trough. I was hoping to feed them all into the new panel through a short section of 2" PVC conduit on a side knockout in the panel. Is this a violation of 312.5(c)? Will I have to run them all individually to the new panel?
I have moved many a panel and have never had to resort to using a trough. I have seen hundreds of residential installations and never have seen a trough.
Before you begin, consider this:
Let's say you are moving the panel to the right. Some of the cables will come from the direction you are moving the panel to. Re-route those and they will all be plenty long enough to hit the panel.
Cables coming from the left and the center that simply won't reach at all, even with a re-route, get spliced in 4 square boxes. We usually do 2 per box.
A typical 10 circuit job will have 5 circuits that reach and 5 that won't. In that case, I would use 2 4S deep boxes, one with two circuits and one with three, or if it's easy reach, put up three and do 2, 2 and one. Popping up three boxes is easier than a trough and looks better, too.