question about nec exam prep 20008
warrenl
New member
question #18 under unit 1 practice questions gives a value of 12.90 ohms for the value of K. I'm sure it's obvious but I do not know how how to find that value, or I have forgotten please help.
charlie b
Lockport, IL
Retired Electrical Engineer
We have no way of knowing what book you are getting your practice questions from. A lot of companies publish practice exam books. So I cannot be sure what "K" means, in the context of that book. Can you be more specific?
Welcome to the forum.
raider1
Logan, Utah
Welcome to the forum.:)
If this question is in regards to voltage drop calculations then 12.9 is the resistance of 1000 circular mils of copper at 1000 feet.
This is a standard value (K) used for a copper conductor with many voltage drop formulas.
Also "K" for aluminum conductors is 21.2.
Hope this helps.
Chris
bob
Alabama
K varies with temperature. The 12.9 for CU and 21.2 for AL is at 65C. The value at 25C is 10.6 for CU and 17.4 for AL.