I disagree. A watt is a watt. It doesn't matter if the load is 120V or 240V.
And a wittle is a wittle. Sorry I couldn't help my self.
Last edited:
I disagree. A watt is a watt. It doesn't matter if the load is 120V or 240V.
I was going to suggest that the place to start is with the amp meter.$1000. a month bill would be 13.88 KWH at .10 cents. Thats over 50 amps. You should be able to run your amp meter over each branch and find the source or feel each breaker for warmth. Should be obvious.
I've never seen them in the attic either. They are always run inside the walls or ceilings around here. At least they're accessible if something goes wrong if they're not in the slab.
I must be doing something wrong. According to my math, if an electric bill were $1000 in 1 month, and if the rate were 10 cents/KWh (or .10) then that would mean that your usage would have been 10,000 KWh's. Actually just a little less because you have taxes and surcharges and the like that I'm not taking into account here, so I don't understand your math and how you came up with 13.88. Please explain...$1000. a month bill would be 13.88 KWH at .10 cents. Thats over 50 amps. You should be able to run your amp meter over each branch and find the source or feel each breaker for warmth. Should be obvious.
I believe he meant that 10,000 kwh in a month is 13.88 kw, since 10,000/30/24 = 13.88.I must be doing something wrong. According to my math, if an electric bill were $1000 in 1 month, and if the rate were 10 cents/KWh (or .10) then that would mean that your usage would have been 10,000 KWh's. Actually just a little less because you have taxes and surcharges and the like that I'm not taking into account here, so I don't understand your math and how you came up with 13.88. Please explain...
Aha!! Now I get it! Thanks whitney. You are spot on!!I believe he meant that 10,000 kwh in a month is 13.88 kw, since 10,000/30/24 = 13.88.
Wayne
Sorry, the meter will measure accurately with a balanced or unbalanced load. :smile:. . . Would balance bring bill down or do they really measure KWh? . .
I am looking for answer to question of unbalanced load giving higher utility bill. Single phase 240V has 95A on A and 25A on B. Would balance bring bill down or do they really measure KWh?
I know radiant floor heat is available via wiring but all I've seen around here is hot water piping in the concrete slab or hot water piping on the wood subfloor covered with 2" of light weight concrete. I'm doing my new building's concrete floor with hot water radiant heat this fall. You can use a boiler or an electric or gas water heater with circulator pumps. It is pretty economical heat. I have installed electric heat mats for bathroom floors under tile but they are just for specific areas. We put hot water heat piping in a Dr.'s concrete driveway 2 years ago for snow/ice melt.
maybe the roads are kept plowed.I got involved with the radiant heat in a driveway for a Dr. also. I ask why he wanted it " I'm a surgeon and if it snows or ice's I need to get to the hospital". Walk away thinking what about the road that leads to the hospital?