As others have pointed out, when you measure voltage Neutral to Ground, you will see some voltage (just a volt or 3 hopefully) if the circuit is under load. This reading will be half the total voltage drop at that point on the circuit, assuming a number of conditions: the hot and neutral are the same length, there are no bad connections upstream of that point, the neutral is not shared with another circuit, the neutral is not touching the ground downstream of the MBJ, etc. Under load, the hot to ground voltage will be a little higher than the hot to neutral voltage, assuming the above conditions.