jumper
Senior Member
- Location
- 3 Hr 2 Min from Winged Horses
The 120/240 volt limitation has been in place as long as I can remember. With a 120/208 system the grounded conductor is considered a current carrying conductor so you have 3 conductors producing heat. With a 120/240 volt system you only have the equivalent of 2 conductors producing heat.
Actually, the reason for the 120/240V limitation is that the code section was developed by using historical data provided by POCOs for the usage of power of dwelling units and only 120/240V systems were included.