hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
It is possible to get a fairly low level fault, but that is probably an arcing fault and would most likely propagate into a lower resistance fault or self-extinguish, especially at lower voltages. Also, the cables don't instantly fail at their NEC listed ampacity. Refer to the TCC below for a sample of several different THHW conductor size damage curves plotted against a 60A thermal magnetic circuit breaker.
View attachment 2560215
Ok i think i see.
What software you are using? Is it possible to plot the following i have inside fire pump controller and following EGCs load side of the fire pump controller and fire pump? Can you send me in private message if mods are not comfortable for view here??: 450A frame breaker, trip set at 2,118A with EGC size of 2/0 awg copper, 350 kcmil copper and 750 kcmil copper plotted?