77401 said:What is wrong with that? What is a field assembled cord. I have appliance cords on the truck I install on DW's.
422.16B2
Are you working under the 05 NEC??
Where is the receptacle located??
77401 said:What is wrong with that? What is a field assembled cord. I have appliance cords on the truck I install on DW's.
422.16B2
cpal said:Are you working under the 05 NEC??
Where is the receptacle located??
cpal said:Are you working under the 05 NEC??
Where is the receptacle located??
found out some idiot made a 120 from splicing the 220 in a covered wall last week. drywaller removed the wall in a remodel and found it for me. really ticked me off. must have been there for 10 years or so and when i went to move it the wirenuts fell off.mpd said:I had a similar problem with the hollywood lights in bathrooms, no boxes, grounds cut off, wirenuts pushed back into the wall, not just one contractor I would have to say the majority of contractors, all contractors were notified if it continued to be a problem somebody from the contractor would have to be on site to remove any fixtures I requested for inspection, I have not had any problems with that lately.
check those weatherproof boxes also, failed many contractors no connectors and boxes not grounded
celtic said:Where should it be located...behind the unit or in the next base cabinet?
422.16(B)(2) Built-in Dishwashers and Trash Compactors. Built-in dishwashers and trash compactors shall be permitted to be cord-and-plug connected with a flexible cord identified as suitable for the purpose in the installation instructions of the appliance manufacturer where all of the following conditions are met.
(1) The flexible cord shall be terminated with a grounding-type attachment plug.
Exception: A listed dishwasher or trash compactor distinctly marked to identify it as protected by a system of double insulation, or its equivalent, shall not be required to be terminated with a grounding-type attachment plug.
(2) The length of the cord shall be 0.9 m to 1.2 m (3 ft to 4 ft) measured from the face of the attachment plug to the plane of the rear of the appliance.
(3) Receptacles shall be located to avoid physical damage to the flexible cord.
(4) The receptacle shall be located in the space occupied by the appliance or adjacent thereto.
(5) The receptacle shall be accessible.
infinity said:Here it is:
Sorry...set you up on the trick questioncpal said:If you are connecting to a device in the adjacent base cabinet you are in violation of the minium standards of the NEC.
Do you do any remodels in residential in the field?cpal said:But how do you justify a
purchased cord at a supply center vs "identified as suitable for the purpose in the installation instructions of the appliance manufacturer "????
cpal said:But how do you justify a
purchased cord at a supply center vs "identified as suitable for the purpose in the installation instructions of the appliance manufacturer "????
celtic said:Sorry...set you up on the trick question
422.16(B)(2)(4)
iwire said:Charlie I take that to mean that if the instructions say you may cord and plug connect it than you may buy a UL listed appliance cord and install it that way.
Here is a typical "
Bob
my problem has been field assembled whips innstalled at the job site and ran thru the cabinet base. also some of the instructions that I have encountered have statements such as,
"For models equipped with power cord: Do not modify the plug
provided with the appliance; if it will not fit the outlet, have a
proper outlet installed by a qualified technician."
see http://products.geappliances.com/Pr...MENT=Installation Instructions&SKU=PDW9980LSS
This begs the question(in my mind) if the mfg did not provide the cord set is it permissable to manufacture one or purchase one from another vendor.
Not that it matters but;
I got hung up on this subject because of the change in language between 1996 and 1999. I kinda stuck my foot in it where as I forgot the langugae regarding "adjacent to", I agree it is difficult to install these things without a receptacle in the adjacent base. and I agree the cord and receptacal provides a disconnect. But 400.7 (8) would only allow flexable cord if the appliance is intended or identified for such use. I see a conflict between the two articles and the inconsistancy in the manufactures instructions.
Also when this new language first appeared in the NEC ref to (96 language) the proposal statements indicated that tme mfg standard restricted the use of cords on appliances unles it was a kit identified by the manufacture.
That language did not find it's way into the NEC (so it's not enforceable unless in the installation instructions).
cpal said:Bob my problem has been field assembled whips innstalled at the job site and ran thru the cabinet base.
also some of the instructions that I have encountered have statements such as,
"For models equipped with power cord: Do not modify the plug
provided with the appliance; if it will not fit the outlet, have a
proper outlet installed by a qualified technician."
This begs the question(in my mind) if the mfg did not provide the cord set is it permissable to manufacture one or purchase one from another vendor.
But 400.7 (8) would only allow flexible cord if the appliance is intended or identified for such use.
iwire said:if the instructions show how to install a cord the appliance is in fact intended for cord and plug connection.
At first I found it surprising but after some more thought it actually makes good sense.