That is only allowed per raceway as 300.3(B) requires all conductors (including the grounding conductor) of a circuit to be in the same raceway.250.122(C) Multiple Circuits. Where a single equipment grounding conductor is run with multiple circuits in the same raceway or cable, it shall be sized for the largest overcurrent device protecting conductors in the raceway or cable.