question from student
domnic
Electrical Contractor
i have a 100 amp service 120/240 with a #6 GEC gowing to a ground rod at what points on the service can i connect the other end of the GEC TO THE SERVICE.
Re: question from student
250.36(F) At any point from the grounded side of grounding connection at the service equipment or the system disconnecting means.
250.53(D)(2) If it's a supplemental electrode, it can be bonded to the grounding electrode conductor, the grounded service conductor, the non flexible grounded service raceway or any grounded service enclosure.
[ March 03, 2004, 03:13 AM: Message edited by: russ ]
Strike the 250.36(F) reference.
250.24(B)is where you will find it.
[ March 03, 2004, 03:14 AM: Message edited by: russ ]