i cant remember if they gave me that info, that was goin to be my next question on table 348.22 they give you wire type and if its inner or outter.

on the test it said. flexible metal tubing a #14 awg ground how many can you add.

again maybe i cant remember if they asked inside or outside i will be more prepared this time
 
Without knowing whether or not the fitting is inside or outside you can't really answer the question correctly.

Chris
 
i cant remember if they gave me that info, that was goin to be my next question on table 348.22 they give you wire type and if its inner or outter.

on the test it said. flexible metal tubing a #14 awg ground how many can you add.

again maybe i cant remember if they asked inside or outside i will be more prepared this time


Article 348 is for flexible metal conduit. Flexible metal tubing is something different and covered under Article 360.
 
Rob i just took the test and yes article 360.22-B takes me back to 348.22 on the 3/8, on the number of conductors aloud,no one has given me an answer on how many conductors are aloud in this question that was on the test.

there is no table on conductors aloud on 3/8 flexible metal tubing, do i still use table 348.22.
 
Rob i just took the test and yes article 360.22-B takes me back to 348.22 on the 3/8, on the number of conductors aloud,no one has given me an answer on how many conductors are aloud in this question that was on the test.

there is no table on conductors aloud on 3/8 flexible metal tubing, do i still use table 348.22.


Yes you're correct, I should have included that in my post. :smile:

The inside or outside connector is the information that you really need to accurately answer the question.
 