I agree. :smile:Floor, not driveway.
I agree. :smile:Floor, not driveway.
501.10 Wiring Methods. Wiring methods shall comply with 501.10(A) or (B).
(A) Class 1, Division 1.
(1) General. In Class 1, Division 1 locations, the wiring methods in (a) through (d) shall be permitted.
(a) Threaded rigid metal conduit or threaded steel intermediate metal conduit.
Exception: Type PVC conduit and Type RTRC conduit shall be permitted where encased in a concrete envelope a minimum of 50 mm (2 in.) thick and provided with not less than 600 mm (24 in.) of cover measured from the top of the conduit to grade. The concrete encasement shall be permitted to be omitted where subject to the provisions of 514.8, Exception No. 2, and 5I5.8(A). Threaded rigid metal conduit or threaded steel intermediate metal conduit shall be used for the last 600 mm (24 in.) of the underground run to emergence or to the point of connection to the aboveground raceway. An equipment grounding conductor shall be included to provide for electrical continuity of the raceway system and for grounding of non-current-carrying metal parts.
I say this should not apply to a garage. Any engineer worth his salt will reinforce the concrete to handle the appropriate loads.
I have the official ruling from the meeting . .
This is not an official interpretation of Code Making Panel 3 so it is not really an official ruling and carries no weight. However, I agree with Mark and the rest of the panel. Mark is the Electrical Engineering Division Manager, runs the staff at the Code Panel Meetings, and is the Secretary of the Technical Correlating Committee meetings. Additionally, I believe Mark is a EE and PE but I am not sure of either one of those guesses.This question was answered . . . by Mark Early . . . The response was Table 300.5 zero clearance under the building. . .
I thought this was a good question and was wondering what you all thought.
In wiring a new car dealership we installed PVC Schedule 40 conduit under the slab of both the office area and service areas of the dealership. We scratched the PVC into the sand base under the floor slabs but the inspector has required the PVC to be buried 24*inches deep in the service areas as vehicles will "drive over the floor making it a driveway." What is your opinion?
This is not an official interpretation of Code Making Panel 3 so it is not really an official ruling and carries no weight.
I can understand that opinion and think it can be justified. I will also say I never understood the 2' cover rule for conduits under a concrete driveway.
Well, regardless of Mark's credentials, I'm going to have to disagree with his interpretation :grin:This is not an official interpretation of Code Making Panel 3 so it is not really an official ruling and carries no weight. However, I agree with Mark and the rest of the panel. Mark is the Electrical Engineering Division Manager, runs the staff at the Code Panel Meetings, and is the Secretary of the Technical Correlating Committee meetings. Additionally, I believe Mark is a EE and PE but I am not sure of either one of those guesses.
I suppose with the heavy weight of tractor trailers and the heaving of the soil from frost etc. the conduits are safer down at 2'. Pot holes can get big at times and then there is Florida --- well you know the rest of the story.
I've got it! Have the architect re-designate the area as a runway!If you cross under an airport runway your cover requirement is less. Interesting.
Is the intent of the 24" under streets, highways, roads etc, because of the heavy loads or because they are dug up and repaired