KWH

Senior Member
I am needing to add a panel from an existing MDP but I don't need the high leg for any loads, when calculating new load at this panel you would divide your total va by 240 and not 240x 1.73 is this correct.

Thanks
 
You are correct and you wouldn't need to install the high leg in this new panel if it's not needed.

Roger
 