K KWH Senior Member Feb 17, 2015 #1 I am needing to add a panel from an existing MDP but I don't need the high leg for any loads, when calculating new load at this panel you would divide your total va by 240 and not 240x 1.73 is this correct. Thanks
I am needing to add a panel from an existing MDP but I don't need the high leg for any loads, when calculating new load at this panel you would divide your total va by 240 and not 240x 1.73 is this correct. Thanks
roger Moderator Staff member Location Fl Occupation Retired Electrician Feb 17, 2015 #2 You are correct and you wouldn't need to install the high leg in this new panel if it's not needed. Roger
You are correct and you wouldn't need to install the high leg in this new panel if it's not needed. Roger
K KWH Senior Member Feb 17, 2015 #3 roger said: You are correct and you wouldn't need to install the high leg in this new panel if it's not needed. Roger Click to expand... Thanks Roger
roger said: You are correct and you wouldn't need to install the high leg in this new panel if it's not needed. Roger Click to expand... Thanks Roger