Just built a new house recently and want to add an ethernet drop in my master. I found a nice drop that goes right to the basement. I wanted to know if it's safe under code to run CAT6 CMP, in the same metal conduit as the 18awg CL2 doorbell run. From what I've seen online it looks like it's ok and shouldn't cause much if any interference. Just wanted some a second opinion. Thanks, Tony.
725.139(E) Class 2 or Class 3 Cables with Other Circuit Cables.
Jacketed cables of Class 2 or Class 3 circuits shall be permitted in the same enclosure, cable tray, or raceway with jacketed cables of any of the following:
1) Power-limited fire alarm systems in compliance with Article 760
2) Non-conductive and conductive optical fiber cables incompliance with Article 770
3) Communications circuits in compliance with Article 800
725.139(E) Class 2 or Class 3 Cables with Other Circuit Cables.
Jacketed cables of Class 2 or Class 3 circuits shall be permitted in the same enclosure, cable tray, or raceway with jacketed cables of any of the following:
1) Power-limited fire alarm systems in compliance with Article 760
2) Non-conductive and conductive optical fiber cables incompliance with Article 770
3) Communications circuits in compliance with Article 800