buckofdurham said:Then what about a 400 amp service with 2 - 200 amp main disconnects. Obviously you would go to the meter base.
But that could also be a meterbase combo
tonyou812 said::-? Ive always been under the impression that, lets say in a residential service lateral one could connect the GEC to the meter pan, or the main ocpd but if You read 250.24(A)(1)
Thank you you've got me right again. now it makes sense againcrossman said:It may have already been said, but it seems your friend applied "the service disconnecting means" at the end of the sentence to the entire sentence. It actually only applies to the t"erminal or buss" part. For example:
General. The grounding electrode conductor connection shall be made at any of the following:
1. an accessible point at the load end of the service drop or service lateral
2. an accessible point at the terminal or buss to which the grounded service conductor is conneted at the service disconnecting means.
3. any accessible point between 1 and 2.
Sorry if this is redundant.