Does every 2-inch LB have adequate dimensions to hold 3 - 3/0 AWG conductors. Specifically do all 2-inch LB fittings comply with 314.28 (A)(2)exception? If not, how is the installer to know if 3/0 conductors may be installed.
Thank you
Brian Dolan
 
Re: Question on Conduit Fittings

heck, I'm prone to a spelling mistake from time and again..I really hadn't, even notice the mistake.

Many thanks for pointing it out Larry.

dillon :)
 
Re: Question on Conduit Fittings

Originally posted by dillon3c:
heck, I'm prone to a spelling mistake from time and again..I really hadn't, even notice the mistake.

Many thanks for pointing it out Larry.

dillon :)
You're welcome, and it wasn't intended as criticizm. Links don't work if they're misspelled.
 
Re: Question on Conduit Fittings

Originally posted by LarryFine:
[/qb]
Links don't work if they're misspelled. [/QB][/QUOTE]

-Laughing-
yes,and I was mildly concerned @ the moment too..

you have a point there brother.. :D

dillon :D
 
Re: Question on Conduit Fittings

Thanks for the help. This is what I learned from UL and Appleton. If a conduit fitting complies with pull 314.28 (A)(1) and (A)(2), there will be no markings on the fitting. Otherwise, it will be marked with the maximum number and maximum size conductors permitted within the fitting.
finhead
 
Re: Question on Conduit Fittings

If a conduit fitting complies with pull 314.28 (A)(1) and (A)(2), there will be no markings on the fitting.
Note that would be a rare fitting. Not very many fittings are sized to meet those rules.