How else can you arrange a delta primary and a star secondary?
I do not know what
has to do with
What current? The transformer was unloaded............For example, 100% of the third harmonic current would pass through the transformer if theywere equal in magnitude and displaced 120o from each other. This flow of current would be just like a balanced three-phase 60 Hertz current.......
I have come across situations like that before where the secondary was similarly distorted with no load on it so it has to have been on the primary side.
The 11kV voltage had the harmonics.then what you saw (the triplen harmonics) came from the magnetizing current of the lightly loaded transformer.
saw plenty of that as well here.
May be so. But the utility may have to provide compensation for that beyond a limit.The 11kV voltage had the harmonics.