Hi Everyone,
I have a quick question regarding MCA, circuit breaker sizing, and conductor size.
If a piece of equipment lists the MCA (Minimum Circuit Ampacity) as 13.3A, my understanding is that the circuit breaker should be at least 15A. The datasheet also lists the "Maximum Breaker" size as 20A. Based on this, I believe a 15A breaker would be acceptable.
I am planning to use #12 AWG copper, but the datasheet mentions that the "Terminal Block to Accept" is #10 AWG. This part is confusing me a little — can I still use #12 AWG if the ampacity is adequate, or do I need to upsize to #10 AWG just to match the terminal block?
Similarly, for an MCA of 17.7A, I believe I should use a 20A breaker. Again, I'm currently planning to use #12 AWG.
Can anyone confirm if my understanding is correct?
Thanks in advance for your help!