Any distribution equipment that can simultaneously receive power from more than one source (e.g. utility and PV) needs to comply.
Cheers, Wayne
I think you may have exceeded my knowledge, so we'll see what others have to say.
But I'm having trouble thinking of a case where the OCPD could be smaller than 125% of the inverter output current. If this is grid-tie, the intervening panelboards might not have any active loads, so there needs to be a feeder path from the inverter to the grid where everything is rated at least 125% of the inverter output current.
Cheers, Wayne
So, my first instinct is that the NEC doesn't let you down-size the OCPD, unless the system is listed as a Power Control System under 2020 705.13 (or you get permission from the AHJ if you are under an earlier version of the NEC). I.e. even though it will work technologically, the regulatory aspect is lagging.Further, energy storage current and PV current will never output into the circuit at the same time (energy storage charges from PV and only outputs after the sun goes down). Although NEC does not care about this fact, this is how we can get away with a smaller OCPD on the critical load panel compared to 125% of total inverter output current.
So, my first instinct is that the NEC doesn't let you down-size the OCPD, unless the system is listed as a Power Control System under 2020 705.13 (or you get permission from the AHJ if you are under an earlier version of the NEC). I.e. even though it will work technologically, the regulatory aspect is lagging.
A one line diagram would be helpful for thinking more about this.
Cheers, Wayne
Well, (2020) 705.30 basically says that the OCPD shall be sized at 125% of the continuous output current rating of the power production equipment, unless elsewhere required or permitted in the NEC. I expect earlier versions have the same language, perhaps in 690 or a different part of 705. So absent the allowance in (2020) 705.13, you have to size the wiring and the breakers for the full output rating of the inverters.
At least, that's my understanding. I know that Tesla Powerwall, for example, now supports limiting the output current in various ways, but I don't know if Tesla has gotten the Powerwall listed as a Power Control System per (2020) 705.13.
Cheers, Wayne
Sure.
When you say microgrid, do you mean there won't be any utility connection? That would put a different complexion on things. If it is grid connected, and the microgrid occurs only when the grid is down, I think that the 705.30 required sizing has to be maintained to the grid.
Cheers, Wayne
How does this code affect upstream panels from the interconnection point? For instance, if PV is tied into a load panel which meets NEC 2017(B)(2)(3), does the main switchgear panel which feeds this load panel also need to comply?
It is my understanding that you are allowed to derate breakers provided that it is behind a locked door or locked equipment panel, so it is only accessible to qualified personnel. It is advisable to apply a label to equipment where code-compliance depends on a field-derating of a breaker, so future site personnel know the correct setting and why.Hmmm. I'm going to provide a one-line as you suggested.
By OCPD I do mean a breaker. Maybe I don't fully understand, why can't you derate an OCPD? Conductor sizes remain the same, so everything is still protected.
For example, if a main breaker was 600A, can I not replace that breaker with a 400A to free up bus space for say a PV installation?
Thanks again!
Utility
|
500A 100% rated service disconnect
|
|--- Feeder Tap based on 1000A Upstream -- Non-Critical Main Breaker Panel
|
Transfer Switch
|
|--- Feeder Tap based on 1000A Upstream -- Critical Loads Main Breaker Panel
|
Generation Panel with 500A Continuous Inverter Output
You haven't drawn in the transfer switch you would need to allow island operation when the grid is down.
Also, I take your drawing to mean that there are PV inverters with a maximum continuous output of 250A, as well as separate storage inverters with a maximum continuous output of 250A
Let me answer your question under two different scenarios (this is all covered under 705.12(B)(2)(3)):
Option A) The PV and storage inverters are interlocked in a way that your AHJ will recognize (e.g. a 2020 Power Control System), and so the combined maximum inverter output current is 250A.
1) Looks OK to me.
2) Breaker 3 is redundant and can match breaker 2 or be eliminated. Breaker 2 needs to be the larger of (a) 125% * 250A (power export) and (b) the NEC calculated load for Load A, Load B, and the storage inverter when it is charging. If the storage only charges from PV and is interlocked in a way that your AHJ will recognize, then that last contribution can be taken to be 0. The bus in the critical panel can be downsized to (80% of Breaker 2) + 250A.
Breaker 1 can be sized the same way as Breaker 2: the larger of (a) 125% * 250A (power export) and (b) the NEC calculated load for all the loads.
Option B) You need to consider that the PV and the storage inverters are both producing 250A simultaneously.
1) You have a number of problems. Breakers 1, 2, and 3 have to be at least 125% * 500A, to start.
2) Sizing is the same as in Option A), but you need to use 500A instead of 250A. The main panel bus needs to be larger.
Cheers, Wayne
P.S. A more efficient connection topology can often be had using (2017) 705.12(B)(1). For example, under Scenario (B), one possibility depending on the load calc, where the vertical line is a 500A Feeder:
Code:Utility | 500A 100% rated service disconnect | |--- Feeder Tap based on 1000A Upstream -- Non-Critical Main Breaker Panel | Transfer Switch | |--- Feeder Tap based on 1000A Upstream -- Critical Loads Main Breaker Panel | Generation Panel with 500A Continuous Inverter Output