OK, you can call it an isolation switch if you prefer. And when the isolation switch is closed and the grid is up, everything is grid tied. So if the none of the inverters are outputting, the critical load panel would be drawing all its power from the grid.
[And obviously in lieu of a 500A 100% rated disconnect, you could use a 700A disconnect and 700A feeder (or 625A and use the next size up rule), but this seemed like a situation where the 100% rated disconnect might pay for itself, worth checking. You could also use a 600A disconnect and shrink one of your inverters slightly.]
Cheers, Wayne
[And obviously in lieu of a 500A 100% rated disconnect, you could use a 700A disconnect and 700A feeder (or 625A and use the next size up rule), but this seemed like a situation where the 100% rated disconnect might pay for itself, worth checking. You could also use a 600A disconnect and shrink one of your inverters slightly.]