I agree with 230.6 when it comes to determining what is allowed inside the building makes this questionable if not in RMC or IMC or encased in 2" of concrete, but what about a metal sleeve (not a raceway) for physical protection of SE cable?I believe that the intent of 230.6(5) is that the service conductors are run in a complete conduit system and not just sleeved, but it doesn't actually say that. 230.92 will require that this conduit be bonded.
I think you meant 250.92 on the second part, but again it doesn't mention short sections for physical protection purposes of a cable that is otherwise not required to be in a raceway.
Quite frankly if the extra physical protection is needed I would more likely just run raceway the entire run but I guess it would be acceptable to sleeve it in places subject to higher level of abuse.