ggunn
PE (Electrical), NABCEP certified
- Location
- Austin, TX, USA
- Occupation
- Consulting Electrical Engineer - Photovoltaic Systems
View attachment HBL.pdf
See attached pdf. Here is a very simplified drawing of a PV system we are building. My contention is that the exception to 690.9(F) says that the 300A fuses on the service side is all the OCPD necessary for the AC side of this system. All the wiring is sized to withstand well over the 300A at 240V and the 36A at 2000V available from the service. The inspector is balking. What say you?
See attached pdf. Here is a very simplified drawing of a PV system we are building. My contention is that the exception to 690.9(F) says that the 300A fuses on the service side is all the OCPD necessary for the AC side of this system. All the wiring is sized to withstand well over the 300A at 240V and the 36A at 2000V available from the service. The inspector is balking. What say you?