Question on Schedule 80 PVC pipe in trench???

Status
Not open for further replies.

jango

Senior Member
Can someone point out the required depth in a trench in general landscaping at a residence for schedule 80 PVC that will contain 120V and 240V wiring? I know schedule 40 is required to be 18" but can the trench be more shallow with schedule 80 PVC? Thanks!
 

dcspector

Senior Member
Location
Burke, Virginia
Can someone point out the required depth in a trench in general landscaping at a residence for schedule 80 PVC that will contain 120V and 240V wiring? I know schedule 40 is required to be 18" but can the trench be more shallow with schedule 80 PVC? Thanks!

See table 300.5
 

Buck Parrish

Senior Member
Location
NC & IN
Yes I agree, Theroy is that a weed eater might "well eat" scedule 40" and not 80. Go figure.
I can't tell much difference. Accept 80 is more brittle.
 

1793

Senior Member
Location
Louisville, Kentucky
Occupation
Inspector
I didn't say there wasn't a difference in the pipe, I said the NEC doesn't recognize it.:)

You are correct, my "bad", I posted to the wrong "Quote".

This is what I thought I was Quoting:

Buck Parrish said:
Yes I agree, Theroy is that a weed eater might "well eat" scedule 40" and not 80. Go figure.
I can't tell much difference. Accept 80 is more brittle.
 
Status
Not open for further replies.
Top