N NYHigh Member Jun 4, 2008 #1 What is the minimum size you can use for a temporary service? What is the minimum size you can use for a regular service? What size PVC for either? Last edited: Jun 4, 2008
What is the minimum size you can use for a temporary service? What is the minimum size you can use for a regular service? What size PVC for either?
resistance Senior Member Location WA Jun 4, 2008 #2 See NEC 230.79 The utility may define the situation for a temp pole.
B benaround Senior Member Location Arizona Jun 4, 2008 #3 NYHigh, I have installed services to highway telephone centers, 120v needed for the 20w light, using #10 wire from WH to meter.
NYHigh, I have installed services to highway telephone centers, 120v needed for the 20w light, using #10 wire from WH to meter.
JohnJ0906 Senior Member Location Baltimore, MD Jun 4, 2008 #4 NYHigh said: What is the minimum size you can use for a temporary service? What is the minimum size you can use for a regular service? What size PVC for either? Click to expand... You would have to check with your local POCO.
NYHigh said: What is the minimum size you can use for a temporary service? What is the minimum size you can use for a regular service? What size PVC for either? Click to expand... You would have to check with your local POCO.
ultramegabob Senior Member Location Indiana Jun 4, 2008 #5 At one time, I worked for a company that was supplying temp poles for a large apt. complex being built. We supplied a bunch of temp poles that were all 50 amp. its probly up to what your poco is willing to connect to...
At one time, I worked for a company that was supplying temp poles for a large apt. complex being built. We supplied a bunch of temp poles that were all 50 amp. its probly up to what your poco is willing to connect to...