Question on wireways 376.22 and derating 310.15 (b) 2

Status
Not open for further replies.

KWH

Senior Member
I do not have to derate with 30 or less conductors in a trough but if there is 34 which percentage in the derating table do you use,

31 thru 34 or 4 thru 6.

Thanks
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The requirement for derating is for 30 CCC's and above, not 30 conductors. You would derate for the total number of CCC's not only the ones in excess of 30.
 