K KWH Senior Member Aug 19, 2011 #1 I do not have to derate with 30 or less conductors in a trough but if there is 34 which percentage in the derating table do you use, 31 thru 34 or 4 thru 6. Thanks
I do not have to derate with 30 or less conductors in a trough but if there is 34 which percentage in the derating table do you use, 31 thru 34 or 4 thru 6. Thanks
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Aug 19, 2011 #2 The requirement for derating is for 30 CCC's and above, not 30 conductors. You would derate for the total number of CCC's not only the ones in excess of 30.
The requirement for derating is for 30 CCC's and above, not 30 conductors. You would derate for the total number of CCC's not only the ones in excess of 30.