Hi,
My boss tends to "bend" to the requests of the inspector(s) more easily than I wood. He has good reputation with inspectors and maybe he figures that in the long run it is better to pick your battles. I don't necessarily disagree with this, but perhaps I draw the line a little differently than he would.
On a swrvice (which I did) he was present for the inspection and the install failed for three reasons.
1) The grounded service donductor had a splice.
2) The ground rods were attached to the cold water pipe, but the conductor did not continue to the panel. The GEC was a seperate conductor which also attached to the water pipe 3' away (within 5' of the point of entry of the building).
3) There was splicing tape over one service conductor that was nicked during installation.
My comments to my boss were:
1) 230.46 specifically allows for splicing of service conductors. It does not specify grounded or undgounded.
2) 250.52(D)2 "exception" allows me to attach to the water pipe and does not require that the conductor continue to the service panel.
3) I don't have a code section on this one, but I don't know why a nick in a service conductor wouldn't be allowed to be protected with a wrap of rubber tape followed by a covering of electrical tape.
I guess what I am looking for is this. Do you agree that the service is OK? If not, where are the problems. And second, if you agree it's OK, any suggestions for dilpomatically explaining that I'd like to convince the inspector that the install is OK rather than go repull 40' of 2/0 wire for for no good reason. (see, profit sharing does work
Thanks for your input
My boss tends to "bend" to the requests of the inspector(s) more easily than I wood. He has good reputation with inspectors and maybe he figures that in the long run it is better to pick your battles. I don't necessarily disagree with this, but perhaps I draw the line a little differently than he would.
On a swrvice (which I did) he was present for the inspection and the install failed for three reasons.
1) The grounded service donductor had a splice.
2) The ground rods were attached to the cold water pipe, but the conductor did not continue to the panel. The GEC was a seperate conductor which also attached to the water pipe 3' away (within 5' of the point of entry of the building).
3) There was splicing tape over one service conductor that was nicked during installation.
My comments to my boss were:
1) 230.46 specifically allows for splicing of service conductors. It does not specify grounded or undgounded.
2) 250.52(D)2 "exception" allows me to attach to the water pipe and does not require that the conductor continue to the service panel.
3) I don't have a code section on this one, but I don't know why a nick in a service conductor wouldn't be allowed to be protected with a wrap of rubber tape followed by a covering of electrical tape.
I guess what I am looking for is this. Do you agree that the service is OK? If not, where are the problems. And second, if you agree it's OK, any suggestions for dilpomatically explaining that I'd like to convince the inspector that the install is OK rather than go repull 40' of 2/0 wire for for no good reason. (see, profit sharing does work
Thanks for your input