Im trying to figure out what the heck is going on at my wifes tanning. All the beds have disconnects in the room and in one room in particular, the breaker keeps tripping and I'm trying to figure out what the heck is going on. Heres some better details:
*In the room is square D breaker 80a
#6 thhn running from dis connect to main panel to another 80a breaker
Bed will run full cycle(7 minutes) and usually trip towards end or if I reset and try and run again
So I hooked up a clamp meter to the lines at the bed from the disconnect and it was like 62a running. Then i checked line between disconnect and main panel and like 100a??? What the heck is that.
So now im really confused. I was hoping for just a bad breaker but now im lost. Can anyone give me some insight here.