I have a few questions about single phase loads on a 3 phase 120/208 panel. Prior to my joining the site I have searched dozens of threads on here trying to find the answer and did not find conclusive answer.
To start I do estimating for a company that builds large prewired chef’s counters for commercial kitchens in restaurants and stadiums etc.
I have a customer who’s engineer sent me a change to a panel layout that in one way makes sense in another seems to not. Due to the nature of the business most of these will be constant loads as they will all be on during business hours. Several are food warmers that are inductive loads and the others are refrigerators or freezers. No lighting or non-dedicated outlets. All are 120v there are No 3 phase items on this panel. This is UL listed and NO additions or modifications are allowed after the fact without voiding the UL listing.
My main question is in sizing the panel (biding the right panel), when converting to amps as per normal the total is 97.1 amps @ 120v this was originally a 125amp single phase panel that the engineer now wants to change to a 3 phase 60amp panel.
Can some of you guys help me understand how this panel should be sized. I get that the load per leg is what it is, but the overall total load is 97.1amps right????? I am hoping to understand more not just an answer of XXX amp panel if you know what I mean. Thank you all in advance for your help. Dave
3 Phase Panel layout as follows
Bus A Bus B Bus C
.95kva .95kva .95kva
.95kva .876kva .876kva
1.1kva 1.1kva 1.1kva
.360kva .924kva 1.1kva
.360kva__________________
3.7kva 3.8kva 4kva = 11.5kva Total
To start I do estimating for a company that builds large prewired chef’s counters for commercial kitchens in restaurants and stadiums etc.
I have a customer who’s engineer sent me a change to a panel layout that in one way makes sense in another seems to not. Due to the nature of the business most of these will be constant loads as they will all be on during business hours. Several are food warmers that are inductive loads and the others are refrigerators or freezers. No lighting or non-dedicated outlets. All are 120v there are No 3 phase items on this panel. This is UL listed and NO additions or modifications are allowed after the fact without voiding the UL listing.
My main question is in sizing the panel (biding the right panel), when converting to amps as per normal the total is 97.1 amps @ 120v this was originally a 125amp single phase panel that the engineer now wants to change to a 3 phase 60amp panel.
Can some of you guys help me understand how this panel should be sized. I get that the load per leg is what it is, but the overall total load is 97.1amps right????? I am hoping to understand more not just an answer of XXX amp panel if you know what I mean. Thank you all in advance for your help. Dave
3 Phase Panel layout as follows
Bus A Bus B Bus C
.95kva .95kva .95kva
.95kva .876kva .876kva
1.1kva 1.1kva 1.1kva
.360kva .924kva 1.1kva
.360kva__________________
3.7kva 3.8kva 4kva = 11.5kva Total