You can, but it is a single shot scenario for getting kVA here.
We know that 208 x 1.732 = 360 and 120 x 3 = 360, so 90 x 120 is the same as 30 x 208 x 1.732 or (360) works because we know the variables.
But later with any 208V loads it does not. Cannot just continue add amps.
It is a limited method that can easily lead to future errors, so I prefer not to even present to people just learning.
OP keeps getting confused and uses that number thinking he needs a 100A panel like his supply guy.
It is simply bad methodology to present it to noobs IMO.