Questions Regarding Connection Made at Feeders

Frank6172

Member
Location
Maryland
Occupation
Engineer
Hi all,

Please take a look at the attached draft of interconnection plan. To avoid the trench we plan to make the interconnections at each building instead of a homerun. Is there any problem on this preliminary design?

Thanks in advance!
 

Attachments

  • Governor Square Question on 1-Line.pdf
    188.2 KB · Views: 9
The general idea is fine by the NEC. Utilities have their own rules about how many PV disconnects they'll allow and their location requirements so I can't speak to that; you'll have to check with the utility if you don't already know their rules.

If the 400A disconnects shown at each building are fused and immediately adjacent (or even just close enough) to the tap points, I don't think the conductors between the taps and the disconnects need to be upsized. The taps to the PV disconnects should follow the tap rules in 240.21(B). If a single fused disconnect for each system cannot be placed to meet the taps rules, utility requirements, and 690.15 requirements for disconnects at the inverters, then you might need additional disconnects.

One other spot bearing some additional scrutiny is the conductors between the transformer @ building 2 and the tap point at Building 3. What transformer secondary rule (240.21C) do these follow? It may be that you cannot tap these conductors without putting an additional overcurrent device ahead of the tap. (Or maybe one already exists but is just not shown?)

Utility requirements aside, the general idea to interconnect at each building to avoid trenching is sound by the NEC, and these other details I've mentioned are just details.
 
The general idea is fine by the NEC. Utilities have their own rules about how many PV disconnects they'll allow and their location requirements so I can't speak to that; you'll have to check with the utility if you don't already know their rules.

If the 400A disconnects shown at each building are fused and immediately adjacent (or even just close enough) to the tap points, I don't think the conductors between the taps and the disconnects need to be upsized. The taps to the PV disconnects should follow the tap rules in 240.21(B). If a single fused disconnect for each system cannot be placed to meet the taps rules, utility requirements, and 690.15 requirements for disconnects at the inverters, then you might need additional disconnects.

One other spot bearing some additional scrutiny is the conductors between the transformer @ building 2 and the tap point at Building 3. What transformer secondary rule (240.21C) do these follow? It may be that you cannot tap these conductors without putting an additional overcurrent device ahead of the tap. (Or maybe one already exists but is just not shown?)

Utility requirements aside, the general idea to interconnect at each building to avoid trenching is sound by the NEC, and these other details I've mentioned are just details.
Thanks very much for your response Jaggedben! I somehow ignored the 240.21(B) tap rule and that's a good point. Maybe I was thinking supply side connection where the tap rule does not apply.

We did find out the OCPD ahead of the tap point which is the 300A fuses shown below. Our utility allows (6) maximum PV disconnects for one utility service(There's only one utility meter in Building 1). I just updated the preliminary 1-Line and I will update this thread if we hear any comments from the utility.