hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have incoming service conductors going to utility meter and then to service disconnect. 705.12(A) says I am permitted to be connected to the supply side of the service disconnecting means as permitted in 230.82(6). I have provided a junction box and would be tapping service conductors to the PV AC disconnect between the utility meter and service disconnect but NOT inside the service disconnect line side breaker terminal.
The inspector is saying what is done is not the intent of NEC 2014 Article 705.12(A). The tap needs to be made inside the service disconnect and on the line side of the service breaker terminal. Is the inspector correct about this one?
The inspector is saying what is done is not the intent of NEC 2014 Article 705.12(A). The tap needs to be made inside the service disconnect and on the line side of the service breaker terminal. Is the inspector correct about this one?