David Fernandes
Member
I have a receptacle that gives the following voltage. 120v from hot to nut. 70v from hot to ground. 50v from nut to ground. Any clues?
I have a receptacle that gives the following voltage. 120v from hot to nut. 70v from hot to ground. 50v from nut to ground. Any clues?
The panal meter is digital.
Did you check for a bootleg connection, a bootleg neutral, can produce these readings. We usually find them in switch boxes, where some jack leg used the ground wire, for a neutral, happens a lot, where they add recess lighting.
Did you check for a bootleg connection, a bootleg neutral, can produce these readings. We usually find them in switch boxes, where some jack leg used the ground wire, for a neutral, happens a lot, where they add recess lighting.
What's a jack leg? I have heard of bootleg whiskey, bootleg music, and even a switch leg. But a jack leg?
Tieing the neutral and ground together at a device to make it appear it's grounded when using a plug-in tester.
Tieing the neutral and ground together at a device to make it appear it's grounded when using a plug-in tester.
Hey that's cheating!
This will also work for a GFIC. I would not recommend it.
What's a jack leg? I have heard of bootleg whiskey, bootleg music, and even a switch leg. But a jack leg?
Not to mention unsafe as all git-out.
That is a GFCI.
A GFCI does not need an EGC...
GFCI. GOT IT... Thank you. That helps a lot.