For a quick way to calculate a minimum neutral size, could you base that calculation on the ungrounded conductors or breaker?
e.g. 3ph 4 wire service/feeder 600A breaker. The first 200A at 100% and then the balance of 400A at 70% = 200 + (.70 * 400) = 200 + 280 = 480A
e.g. 3ph 4 wire service/feeder (2) 500MCM AL XHHW rated 620A. The first 200A at 100% and then the balance of 420A at 70% = 200 + (.70 * 420) = 200 + 294 = 494A = (2) 350MCM
This idea just popped into my head as I read Article 220 and I'm blurting it out.
e.g. 3ph 4 wire service/feeder 600A breaker. The first 200A at 100% and then the balance of 400A at 70% = 200 + (.70 * 400) = 200 + 280 = 480A
e.g. 3ph 4 wire service/feeder (2) 500MCM AL XHHW rated 620A. The first 200A at 100% and then the balance of 420A at 70% = 200 + (.70 * 420) = 200 + 294 = 494A = (2) 350MCM