If I have all single phase loads on a 3 phase panel, which calc. do I use?
1. Watts (19951) / Volts (208) = 96A
or
2. Watts (19951) / Volts (208) x 1.73 = 166A
Thanks,
How about total load watts / 3 / L-N volts, presuming balanced loading (and a Y system).If I have all single phase loads on a 3 phase panel, which calc. do I use?
You either have to divide by the sqrt(3) or "group" volts times sqrt(3):2. Watts (19951) / Volts (208) x 1.73 = 166A
Bob,
I don't know why, but I just can't come up with 74A any way I do it.
I can come up with 55.44A
What steps are you taking?
Thanks,