Re: Raceway as EGC
This thread is really getting into motion!
Bennie has brought up a very important key issue with the GFPE for >150VAC to Ground, upto 600VAC L-L, 1,000 Amps and larger services.
The Arc Fault on these Wye connected 4 wire systems will be frying away for days - and the OCPD just looks at it as an unstable Transiently Peaking Load - so no trip!
So the GFPE is used - very similar to the method behind GFCIs, to trip incase of an excessive Ground fault Current (more like excessively unbalanced load currents measured).
The CT used (Donut) has all 4 wires run through it.
So, why do only 4 wire Wye systems have this problem, and 3 Wire Deltas do not (above 150VAC to Ground, upto 600VAC L-L, 1000 amps and larger).
Hint: Look at the connection schemes of each Transformer's setup.
Now here's something totally different to ponder:
An OCPD activates from an Overcurrent / Overload situation, right?
Say the Loop Impedance was great enough on a Circuit (Circuit Conductors + EG paths), to allow only 35 amps flow on a 20 amp circuit.
Is this still a Ground Fault?
Since this flows to Ground, will the 35 Amps ever trip an OCPD with a 20 Amp rating?
Of course it will! It won't trip fast, it might trip after 15 minutes, but it will eventually trip.
Besides the Shock Hazards to Personnel, will this pose any other dangers to the system or Building?
This should get some different views indeed!
Super Bonus Question!!!
What will result from the following:
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">120/240V 1? 3W 37.5 KVA Transformer - Z = 2%,</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Transformer is 20 feet from Panelboard,</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Panelboard is 200 Amp bus, fed with 3 # 3/0 CU + 1 #1 cu for the EGC,</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Branch Circuit has 40 Amp OCPD - 10KAIC,</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Branch Circuit is 2 #6 cu, 1 #8 cu EGC - 1" Aluminum IMC,</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Six 5 HP 1? Cap. start Induction Motors running on system, loaded to 90% capacity,</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Ground Fault on the above Branch Circuit occurs 10 Feet from Panelboard.</font>
<font size="2" face="Verdana, Helvetica, sans-serif">
What happens if we swap the #6s with #10s?
What if we increase the KVA to 75 KVA, or 112.5 KVA with Z = 1.4%?
What if we move the Transformer farther away, use smaller feeders and higher %Z?
What if the Ground Fault occurs 100 feet away from Panelboard?
What if all the Motors were starting at the time of the Fault?
What if all the Motors shut off at the time of the Fault?
What if both Ungrounded Conductors Fault to Ground at the same time?
To most, these will be easy - even laughably simple! To others, it might be a bit difficult at first. Some may not know there's any difference, or know of these factors - which is why I wanted to toss this in and get some feedback.
I picked the numbers at random, so feel free to do the calcs and post them.
Scott35