ramsy
NoFixNoPay Electric
- Location
- LA basin, CA
- Occupation
- Service Electrician
See 250.102(E) if within 6ft of equipment.EGCs have to run with the circuit conductors. They are not permitted to be run by themselves.
If over 6ft, see 250.102(E) Exception