Can someone tell me if there is a code issue with the entrance raceway and the exit raceway being so close to each other? I there a minimum distance they need to be from each other? Where would I be able to find this in the NEC?
Yes, there is a problem there.
That is an angle pull and by code for #4 and larger there should be 6x2=12 inches between those nipples if they are 2 inch nipples and if the wires are #4 or larger.
I think we are looking at 6 AWG supplying a 60 amp outlet.
Ugly but not a violation.
Ummmmm, that looks like a 200 amp inlet or receptacle to me.
And it looks like it is 3/0 wire with a 1/0 ground.
those are 2 inch nipples also at least the one through the back of the box.
I wish I could enlarge tha picture.
Can the OP verify the wire size and rating of the Inlet?
Boy, I don't know, look at the GFCI outlet on the bottom right.
There is no way that looks like a 2" with 3/0 to me.
Maybe 1.25" with 3 AWGs?
use an LB & be done with it :happyyes:
use an LB & be done with it :happyyes:
that is a 200a generator plug being fed by 3/0 and #2 ground through 2"pipe. i have already had my production crew replace this with a 2"LB. i went off of 314.28
So it's an outlet, not an inlet?
JAP>
It sounds like a 702.7(C) Power Inlet.
The typical LB has to comply with 314.28(A)(3) as they don't have the length that would be required by 314.28(A)(2) for angle pulls. So my question is, what was the marking on the LB? I have never seen a marking that said more than 3 conductors and there is no provision to do a field calculation.that is a 200a generator plug being fed by 3/0 and #2 ground through 2"pipe. i have already had my production crew replace this with a 2"LB. i went off of 314.28
The typical LB has to comply with 314.28(A)(3) as they don't have the length that would be required by 314.28(A)(2) for angle pulls. So my question is, what was the marking on the LB? I have never seen a marking that said more than 3 conductors and there is no provision to do a field calculation.