That can trigger another issue with LB about that size. 314.23(E) requires independent support of a conduit body that has a trade size larger than the trade size of the conduit, where the volume of the conduit body exceeds 100 cubic inches. Some 2 1/2 LB have a volume that exceeds 100 cubic inches.We step our LB's up to 2-1/2 for that reason.
Also, if that is a 4 pole 4 wire inlet or outlet I believe the minimum wire size for the pins is 1/0. But I would have to see the paperwork that came with it.
Note, I have never seen this done in the field and I have installed oversized conduit bodies many times without independent supports.