Raceway in Two Different Ambient Temperatures

Status
Not open for further replies.
Location
Newtown, CT, USA
Occupation
Engineer
I have a raceway partially in 35C and partially in 60C; say, six feet of 35C and two feet of 60C, or 4 feet of 35C and a foot of 60C. Are there any regulatory provisions for this scenario quantifying how much of the run needs to be in 35C before I can derate my conductors per 35C instead of 60C? Or do I have to measure or simulate or calculate an "average ambient" temperature?
 

drktmplr12

Senior Member
Location
South Florida
Occupation
Electrical Engineer
I have a raceway partially in 35C and partially in 60C; say, six feet of 35C and two feet of 60C, or 4 feet of 35C and a foot of 60C. Are there any regulatory provisions for this scenario quantifying how much of the run needs to be in 35C before I can derate my conductors per 35C instead of 60C? Or do I have to measure or simulate or calculate an "average ambient" temperature?

if one section of conductor is subjected to 60C ambient, i would derate the entire thing.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
I have a raceway partially in 35C and partially in 60C..
In new construction AHJ's, and their planning department might help solve this question.

For such short lengths, placing smaller raceway inside larger insulating pipe may also deflect some heat away from short lengths under 10ft. Temperature probe readings would confirm heat shielding efforts.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I have a raceway partially in 35C and partially in 60C; say, six feet of 35C and two feet of 60C, or 4 feet of 35C and a foot of 60C. Are there any regulatory provisions for this scenario quantifying how much of the run needs to be in 35C before I can derate my conductors per 35C instead of 60C? Or do I have to measure or simulate or calculate an "average ambient" temperature?

Although they might not apply to short runs there are provisions in the NEC to disregard certain higher ambient temperature sections of a run.

310.15(A)(2) Selection of Ampacity. Where more than one ampacity applies for a given circuit length, the lowest value shall be used.
Exception: Where two different ampacities apply to adjacent portions of a circuit, the higher ampacity shall be
permitted to be used beyond the point of transition, a distance equal to 3.0 m (10 ft) or 10 percent of the circuit
length figured at the higher ampacity, whichever is less.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
Thanks for the helpful responses! I like the idea of insulation/heat deflection and measurements to verify effectiveness, if permitted by authorities.

Julia
Isn't there a ten foot, ten percent, whichever is less rule?
 
Location
Newtown, CT, USA
Occupation
Engineer
See post #4.

Yes, sorry, I did see that, I just had trouble parsing it.

"the higher ampacity shall be permitted to be used beyond the point of transition"

seems to be saying that I'm allowed to change to smaller conductors at the point of transition? Like add a junction box and splices? That can't be right, can it?
 
Location
Newtown, CT, USA
Occupation
Engineer
They way I read it, it’s either 10 FT or 10%, not “and”.

You're allowed to go 10ft, or you're allowed to go 10%, whichever is less. So if 10% is less than 10ft, you're not allowed to go 10ft, and if 10ft is less than 10%, you're not allowed to go 10%. Therefore whatever distance you want to run at the higher ampacity has to be both less than 10ft and less than 10% of the total circuit. Or else I need more coffee...
 

retirede

Senior Member
Location
Illinois
You're allowed to go 10ft, or you're allowed to go 10%, whichever is less. So if 10% is less than 10ft, you're not allowed to go 10ft, and if 10ft is less than 10%, you're not allowed to go 10%. Therefore whatever distance you want to run at the higher ampacity has to be both less than 10ft and less than 10% of the total circuit. Or else I need more coffee...

You’re correct.

It would have been clearer if the wording was simply “AND” & leave out “whichever is less”.
 