I went to a model center today to review a few of the houses I am considering bidding some work for.

I performed a general walk through and discovered an interesting installtion at the well system equipment. The well equipment is on a 6' by 3' concrete slab with the nearest edge approximately 16" from the house itself. The pump motor is on the slab and is cord-and-plug connected. The receptacle for this is installed on the house. The way the cord gets to the outlet is by means of a 1.5" PVC conduit. The conduit is straped to the slab, 90'd up the wall and ends just below the in-use cover for the receptacle. The entire run is approximatley 24". The cord runs through the pipe, pokes out the other side, and is plug in.

I noticed there was an inspection board still present so I took a look inside to see how the inspections went. Sure enough, two weeks ago there was an advisory that the stated, "the cord for the well pump presents a trip hazard and is exposed to damage from weed eaters and garden tools." A week later, presumably after the handy-dandy conduit install, the job was signed off.

The work is in a jurisdiction north of where I normally work so I am not familiar with who the inspector is or I would ask him what the deal is. Is this in violation of any particular article in the code, and if so, what hazard does this present to warrant the restriction. ?

[ May 11, 2004, 08:16 PM: Message edited by: bphgravity ]
 
Re: Raceway Use Violation

Don't see where the trip hazard is in the NEC but this would be a violation of 400.8.

I would run PVC down the side of the house, buried in the ground and stub up somewhere in the slab before it was poured. On the stub up I would install a box with a receptacle and an in-use cover.

-Hal
 
Re: Raceway Use Violation

I can't see the trip hazard as the space is too narrow, or I am not understanding the desription. Try walking on a surface that is only 16" wide, with one vertical wall, and the items on the wall intrude into the space. Can't get a mower thru there.

Is this equipment listed to be used with cord and plug? Is this another instance where the grounding tang is considered all that is required for the EGC?

paul
 