I can't provide you a numeric reference but I can tell you I failed an OSHA inspection for a identical install and the OSHA rep's statement was both "hub needed and no knockouts allowed"
But not a "Code" thing.
JAP>
314.23(H)(1) is certainly vague, as mentioned previously.![]()
So tell me.
Where in the code does it say that a pendant box cannot have any KO's in it or that it has to have a threaded hub?
JAP>
In 314.23 (H) (1) Pendant boxes suspended by chord, require a strain relief installed into a box with a threaded hub. It's been a requirement as long as I can remember.
the other issue I see is all of the exposed holes in the box for screws... I am pretty sure that exposed boxes like this cannot have those.
No knockouts allowed - you should have knocked all the remaining ones out then you are compliantI can't provide you a numeric reference but I can tell you I failed an OSHA inspection for a identical install and the OSHA rep's statement was both "hub needed and no knockouts allowed"
Just caulked some holes shut the other day in the back wall of a Homeline loadcenter. They were extra "slots" for securing a larger interior when used in the same cabinet. I didn't like how large the opening was considering it was installed in a garage and would be easy entry point for even moderately large insects like wasps. Hate opening equipment and having that surprise.That was another of my thoughts on this installation, however 110.12(A) states that unused openings other than those intended for mounting purposes shall be closed. Those holes are for mounting so I think they don't have to be closed.
So based on everything said here, it seems like it is a valid installation. Not sure if the cord conforms with Table 400.4 which would be something else to look at as well as the support above.
If that were the case, we'd have to caulk the openings on all of our receptacles shut so we couldn't plug anything into them. JAP>
That's what the TR receptacles are for. They're so safe because you can never get the dang plug in!
SceneryDriver
That's what the TR receptacles are for. They're so safe because you can never get the dang plug in!
SceneryDriver
No knockouts allowed - you should have knocked all the remaining ones out then you are compliant
Just caulked some holes shut the other day in the back wall of a Homeline loadcenter. They were extra "slots" for securing a larger interior when used in the same cabinet. I didn't like how large the opening was considering it was installed in a garage and would be easy entry point for even moderately large insects like wasps. Hate opening equipment and having that surprise.
Ok. This is a case of doing something sensible but not required by code
Actually NEC in more recent years added a requirement to bring the neutral to nearly all switches that control lighting outlets, even if the switching device doesn't utilize a neutral.Ok. This is a case of doing something sensible but not required by code, like running a neutral and ground to every switch position. Only certain switch positions require the neutral, but it saves time and cost later if the switch is changed to one that needs the neutral.