inrush comment
inrush comment
Agreed Ron, that it's a safer approach to energize the xfmrs separately.
I grew up in an industrial plant where there were two (2) 15kV breakers that fed three (3) transformers each.
The transformer primaries had 15kV, 600A manual fused switches.
The ideal way to bring the plant up would have been to energize each 15kV line with open disconnects on the xfmr primaries, then close each disconnect switch.
However, the real-world way, and the way that worked, was to never touch the switches - keeping them closed, and energize the each 15kV breaker picking up three (3) transformers at a time.
It was almost a necessity to do it that way because the switches were prone to cable misalignment which was evident during the biannual PMs, where the switches were exercised. On several occasions the switches broke during PM operation, and were left in the closed position until 2 years later when the appropriate parts were replaced.
JM