In addition to being a licensed electrician in VA I also practice real estate; one thing that consistently drives me crazy is the electrical portion of radon mitigation system installations. Most of the time they are of poor quality and make me think "why?".
Just recently I represented the purchaser of a home on a system installation where the contractor hired by the seller nicked a water line when they drilled the drywall in the wrong spot and never said anything because it didn't leak. I'm in the process of getting the company to repair the water line and drywall, I also brought the electrical to their attention because they surface mounted NM and used no connectors on their junction box inside the home. I'm being told that "Systems are installed in the manner that they were approved in the state" and that they do not hire an EC because they are certified to install the systems.
Clearly this installation does not meet code. I've looked up the requirements to be certified in my state as an approved radon mitigation contractor and found that the installer only needs to hold a certification from the NRSB or NRPP, the installing contractor holds a certification and is licensed to operate in my state.
Typically a cord an plug device will carry a UL listing and will not be permanently installed. This system is permanently installed and IMO violates 314.17 Conductors Entering Boxes, Conduit Bodies, or Fittings (for the NM), 400.14 Protection From Damage regarding flexible cords, and 334.15 Exposed Work, & 334.30 Securing and Supporting due to the NM cable being surface mounted with no protection or support.
Is there an exception or code I am missing that would make these system installations exempt? I'm only asking for them to sleeve the NM in FNMC which they already did outside and use a proper cord grip connector for the cord with he molded plug.
Just recently I represented the purchaser of a home on a system installation where the contractor hired by the seller nicked a water line when they drilled the drywall in the wrong spot and never said anything because it didn't leak. I'm in the process of getting the company to repair the water line and drywall, I also brought the electrical to their attention because they surface mounted NM and used no connectors on their junction box inside the home. I'm being told that "Systems are installed in the manner that they were approved in the state" and that they do not hire an EC because they are certified to install the systems.
Clearly this installation does not meet code. I've looked up the requirements to be certified in my state as an approved radon mitigation contractor and found that the installer only needs to hold a certification from the NRSB or NRPP, the installing contractor holds a certification and is licensed to operate in my state.
Typically a cord an plug device will carry a UL listing and will not be permanently installed. This system is permanently installed and IMO violates 314.17 Conductors Entering Boxes, Conduit Bodies, or Fittings (for the NM), 400.14 Protection From Damage regarding flexible cords, and 334.15 Exposed Work, & 334.30 Securing and Supporting due to the NM cable being surface mounted with no protection or support.
Is there an exception or code I am missing that would make these system installations exempt? I'm only asking for them to sleeve the NM in FNMC which they already did outside and use a proper cord grip connector for the cord with he molded plug.