Raised cover
wireday
New England
Master electrician
I have a 30A 250V receptacle that I want to mount to a raised 4x4 steel cover, the cover came with screws & nuts, the receptacle came with the box screws, seems the only choice I have is to use the cover screws without the nuts, as the screws go into receptacle body, wasn’t sure about grounding with that set up,
infinity
New Jersey
Journeyman Electrician
Can you post a photo of the receptacle?
wireday
New England
Master electrician
its a 30A 250V bullseye receptacle no way to use nuts, I don't have luck posting pictures, If you did a search it would come up. The screws go into the threaded holes in receptacle, I do plan on running the EGC to box and receptacle, I have seen many done this way,
synchro
Chicago, IL
EE
If you have a bonding jumper between the receptacle and the box, then you don't need the restrictions on receptacle fasteners in exception (A) of 250.146 to achieve compliant bonding of the receptacle.
SceneryDriver
NJ
Electrical and Automation Designer
Can you just drill two holes in the cover to use screws and nuts?
SceneryDriver
Todd0x1
CA
What's a bullseye receptacle?
hbiss
EC, Westchester, New York NEC: 2014
Hawthorne, New York NEC: 2014
EC