I've had a couple of instances lately that involved existing branch circuit wiring for ranges and clothes dryers in condos. In both instances the equipment was supplied from the service panels in the condos which were not service equipment. The wiring for the ranges and dryers was NM cable with two insulated conductors and and uninsulated EGC. The wiring in both cases was inaccessible.
In the case of the dryer, the 3 slot receptacle was worn out and had to be replaced. In the case of the range, a new range was procured and had to be hooked-up via a 3 slot receptacle. In both cases I connected the frames to the EGC and for the range, connected the range neutral to the EGC also.
The requirements for existing installations spelled out in NEC 250.140 clearly were not met. Did I really screw up by not insisting that the branch circuit wiring be replaced or was what I did OK?
In the case of the dryer, the 3 slot receptacle was worn out and had to be replaced. In the case of the range, a new range was procured and had to be hooked-up via a 3 slot receptacle. In both cases I connected the frames to the EGC and for the range, connected the range neutral to the EGC also.
The requirements for existing installations spelled out in NEC 250.140 clearly were not met. Did I really screw up by not insisting that the branch circuit wiring be replaced or was what I did OK?