is there anywhere in code that allows you to leave a range or dryer that was wired 3 wire as is when adding a new main disconnect panel and subfeed to old panel.
A older house has a 3 wire cable (two hots and a ground/neutral) from a range going to a sub fed panel. Does the ground/neutral wire terminate on the neutral buss or the grounding buss? Personally I think it goes to the neutral buss because it has 120v neutral current from timer and other 120v...
is there anywhere in code that allows you to leave a range or dryer that was wired 3 wire as is when adding a new main disconnect panel and subfeed to old panel.
Milbank 200 Amp 4 Terminal Ringless Side Wireway Underground Meter Socket with Main and Load Center is rated for 200 Amp continuous, 240 Amp maximum up to 600 VAC. This meter socket an 8 circuit breaker
www.homedepot.com
Make sure that your branch circuits comply with 1-4 of the exception to 250.140