Range and dryer services

Status
Not open for further replies.

MissLiz

Member
is there anywhere in code that allows you to leave a range or dryer that was wired 3 wire as is when adding a new main disconnect panel and subfeed to old panel.
 
 
is there anywhere in code that allows you to leave a range or dryer that was wired 3 wire as is when adding a new main disconnect panel and subfeed to old panel.
Use the service equipment in the link below and bring the range and dryer 3-wire branch circuits into this.


Make sure that your branch circuits comply with 1-4 of the exception to 250.140
 