Range hood future microwave code question
I don't have the book in front of me at the moment, but I wanted to know if there was a code requirement to have a 20amp dedicated circuit for a hood over the range in case it is swapped out for a combo microwave/vent hood. The microwave would definitely be pulling a lot of amps. this is not counting the additionally countertop circuits in the kitchen. This is a residential/dwelling unit, not commercial.
Not so fast here - take a look at what is required in 422.16(B)(4).
This section doesn't apply if you "hard wire" the range hood, but if you choose to supply it via cord and plug - you must meet certain requirements with the cord type and length and must have an individual branch circuit - but it doesn't specify it must be a 20 amp circuit.
This section was added (I think) in 2008 NEC but could have been 2011.
It was added in the 2005 NEC.
I have never seen a range hood with a cord and plg connection. That being said I usually run a circuit for the hood just in case a range hood/microwave was added
Been longer then I thought. I generally don't need to pay too close attention though as I usually am running a dedicated circuit (and I always run a 20 amp circuit in these instances even though it doesn't say you have to) because they are installing a microwave hood in maybe about 95% of the installs I do. Or if a higher end home it is often a really fancy range hood and is permanently wired.
Track homes plug their range hoods in all the time out here
Sent from my SM-N900V using Tapatalk
I bet it is not compliant...
422.16(4) Range Hoods. Range hoods shall be permitted to be
cord-and-plug-connected with a flexible cord identified as
suitable for use on range hoods in the installation instructions
of the appliance manufacturer, where all of the following
conditions are met:
(1) The flexible cord is terminated with a grounding-type
attachment plug.
Exception: A listed range hood distinctly marked to identify
it as protected by a system of double insulation, or its
equivalent, shall not be required to be terminated with a
grounding-type attachment plug.
(2) The length of the cord is not less than 450 mm (18 in.)
and not over 900 mm (36 in.).
(3) Receptacles are located to avoid physical damage to the
flexible cord.
(4) The receptacle is accessible.
(5) The receptacle is supplied by an individual branch
circuit.