Another thread showing one advantage of a panel in the kitchen.
allenwayne said:Since I pull 6 20 amp circuits to my kitchens it isn`t a problem.1 fridge,1 d/w, 1 disp 2 s/a and 1 hood micro/hood that is cord connected.But that`s just how i do things.
To me breaker locks are like red lights they are there to stop you but you don`t have to use them.I also cord connect my d/w`s and disposals.
acrwc10 said:Would there be a problem with running in #14 for deticated,refer,disposal,dishwasher,hood,''not micro-hood''.As long as your loads are under the specs? Most disposals and dishwashers are, and hoods dont take more then 3 to 4 amps on the average.since they are not continuous loads I think they dont need any special consideration.
Any input on tying the hood to another apliance if it is just a simple hood fan light unit?
LarryFine said:Another thread showing one advantage of a panel in the kitchen.
iwire said:That said I doubt most home owners want a panel in the kitchen that meets the 110.26 requirments.
acrwc10 said:Would there be a problem with running in #14 for deticated,refer,disposal,dishwasher,hood,''not micro-hood''.As long as your loads are under the specs? Most disposals and dishwashers are, and hoods dont take more then 3 to 4 amps on the average.since they are not continuous loads I think they dont need any special consideration.
Any input on tying the hood to another apliance if it is just a simple hood fan light unit?
Rockyd said:Kithchens are normally a six circuit gig. Fridge,Micro(12/3), dish, insinkerator(12/3), 2sabc's 12/2 each. Ranges are normally 8/3, lights are #14, so why not match the load(s) to small items to, following the 50% rule? Show me a range hood fan/light, for residential that is going to draw 7.5 amps. It's not going to happen in this lifetime. Until it's code though, I can't put it on with a few lights around the kitchen, so we have to drag a circuit in for a 2.5 amp max draw, piece of gear. Maybe 2011, I'll do something about it, proposal could get shot down, but it's an effort the right direction.
Rockyd said:422.16 (4) (5) - The receptacle is supplied by an individual branch circuit. I read individual branch circuit in definitions (art 100) as A branch circuit that supplies only one utilization equipment. he two together are saying that the hood gets it's own circuit.
I think that is totally ridiculous, but the verbage indicates that it's is code. Please correct me, and provide substantiation for the local inspector(s) I deal with. As it stands right now, that's the interpetation I was given, so I have to live with it, no matter what I think, unless there is the right ammunition...
infinity said:If you're asking if the range hood must be on it own circuit the answer is yes if it's cord and plug connected. No if it's hard wired.
allenwayne said:Jim that was my whole point.Bid a dedicated 20 amp. circuit and be done with it.
iwire said:That said I doubt most home owners want a panel in the kitchen that meets the 110.26 requirments.
Here is one of the pics promised..this is a "hi-end" unit - 800k+celtic said:Have I got some pics for you! (well, I will after I shoot 'em)